One hole vs two hole compression lug application

  • E-MAIL

    Votes: 2 66.7%
  • LIVE POST

    Votes: 1 33.3%

  • Total voters
    3
  • Poll closed .
Status
Not open for further replies.

ARCTICSKI

Member
Members of mike holt's forum:


As an electrical inspector, where would you mandate the use of double hole compression lugs, other than when the mating surface is built to accomodate a 2 hole, lug mounting? Give specifics, please

thanks, dave
 

Mike01

Senior Member
Location
MidWest
intresting

intresting

specifications call for 2-hole long barrel double indent...sometimes modified for wire bending space as these will not always fit with the allowable bendng reqruiements of the cable and equipment space avaliable..
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Its never up to the electrical inspector to mandate anything.

Its his job to verify compliance with the applicable requirements, not make up stuff on his own.
 

tom baker

First Chief Moderator
Staff member
The two hole lugs or NEMA lugs, work much better than the one hole for larger wire sizes, say > 1, as the lugs don't twist when tightned. Burndy makes a stacking adapter for conductors in parallel.
 