I'm working on a system design that has a 4160V Delta - 480V Wye transformer with a latching fused contactor on the primary side. The secondary feeds two breakers, through cables bolted onto the secondary bushings. One breaker is somewhat larger than the secondary FLA of the transformer, the second is less than half of the secondary FLA of the transformer.
I understand that NEC Article 240.21(C)(3) could and should apply, but this requires very large cables to a fairly small breaker, and several interested parties don't like this idea.
My question is:
If:
I put CTs on both sets of feeder cables at the transformer secondary,
I connect those CTs to a protective relay with individualized protective functions for each feeder cable,
and I use the protective relay to trip the primary side latching contactor
Then:
Does this qualify as "overcurrent protection...located at the point where the conductors receive their supply"? (Article 240.21)
Thanks!