kingpb
Senior Member
- Location
- SE USA as far as you can go
- Occupation
- Engineer, Registered
Looking at your jpeg, I think you're generalizing a little bit. You don't need to have an adjustable magnetic trip capability on the primary c/b, though it might be required in the example you show. The coordination depends on the specific transfomer and circuit breaker that you are using.
I agree that the NEC rules for transformers don't necessarily protect the transformer, but, if you do proper coordination, you probably could find a transformer/breaker combination that would protect the transformer from through-faults.
Your correct, you wouldn't have to have an "adjustable breaker", but the breaker would need to have a fixed instantaneous trip that was at least 10X the thermal, otherwise it puts you below the inrush.
As far as generalizing, isn't that exactly what the NEC does, is give general guidelines that many people use as the design basis? That's exactly why I showed it as general as possible.
Of course, I can pick breakers that more closely match what I need and get it to coordinate better; perhaps fuses would be better on the HV side. I simply picked standard catalog equipment and plotted it, which is what many are going to do in the field without understanding the consequences. Which, is the whole reason of my point - AWARENESS, i.e. don't just blindly follow the NEC.