Hi Everybody
I need a lot of information on the question i m going to ask.I asked this in other forums but no satisfactory answer.
My excitment started when one day i observed that in one of our transformer (whose secondary winding is delta connected) , the no load voltage is very unbalance with respect to ground.If i check the voltage on secondary side without connecting load to it. It shows 220,220,20. With load these voltages becomes balanced.
I know in transformers with delta secondary , there is no reference to check the voltages.The only thing which is reference is the capacitance with ground.
When i megger the secondary side with cable connected , it gives me reading in gega ohms.
I have two questions.
1) By checking the no load voltages of our transformer , can i say that some of the insulator is week.If yes , then what about the megger value which is very high.
2) If i am using no load voltage in our system for some calculations . Is it possible to make these unbalance voltages balanced in no load conditions.
I guess if i connect some resistors in each phase with ground , it may neglect the ground capacitance as these resistors will behave like small load on transformer.
I need a lot of information on the question i m going to ask.I asked this in other forums but no satisfactory answer.
My excitment started when one day i observed that in one of our transformer (whose secondary winding is delta connected) , the no load voltage is very unbalance with respect to ground.If i check the voltage on secondary side without connecting load to it. It shows 220,220,20. With load these voltages becomes balanced.
I know in transformers with delta secondary , there is no reference to check the voltages.The only thing which is reference is the capacitance with ground.
When i megger the secondary side with cable connected , it gives me reading in gega ohms.
I have two questions.
1) By checking the no load voltages of our transformer , can i say that some of the insulator is week.If yes , then what about the megger value which is very high.
2) If i am using no load voltage in our system for some calculations . Is it possible to make these unbalance voltages balanced in no load conditions.
I guess if i connect some resistors in each phase with ground , it may neglect the ground capacitance as these resistors will behave like small load on transformer.