hi
We are using Siemens make VCB ,rating 2500 A. We observed one day that one phase arm is overheated .I check the current trends and found normal.This is second time we observed this problem.Last time , it was with other phase.
The next step is to measure for voltage drop across the breaker, called 'fall of potential'. This will tell you if there is a restance where there shouldn't ought to be.
hi
We are using Siemens make VCB ,rating 2500 A. We observed one day that one phase arm is overheated .I check the current trends and found normal.This is second time we observed this problem.Last time , it was with other phase.
hello guys
thanks for your comments.
Its a draw out type breaker and operates at around 2000A current.Every 15 days we rack it out during plant shutdown and check visually.
We found the copper arm was over heated which can be seen by the colour of the copper due to heating up.
If the heat was enough to discolour the copper I would have a concern that it may have effected the temper in the spring material, making them weak.
To prove my argument take an IR gun or camera and measure the temperature of each phase and compare it to the load current in each phase to determine if overheating is actually occuring. If not, hire a reputable testing co to do an IR scan and provide you with a detailed report. Also, see if switching can be done to reduce the load below 2000A on this circuit, otherwise you are just asking for trouble.
Good luck!
Tony
Thanks guys
Please see the attached photographs.
Did this breaker interrupt a fault prior to the heat problem ?
hi
We observed one day that one phase arm is overheated .I check the current trends and found normal.