Motor operators for molded case circuit breakers are usually mounted on the front of the breaker. They take the place of your hand pushing the breaker handle between "OFF" & "ON". Most use a small motor driving a worm screw device with overtravel limit switches to cut out the motor.
Motor-Operated, Insulated Case or Air Frame circuit breakers have the motors and spring charging mechanisms mounted internally like the above picture shows. It takes the place of manually cranking the handle to charge the closing spring.
Some large breakers close as soon as the spring is fully charged and the motor drives the charging cam past top dead center. But most breakers are designed with a separate "Close" solenoid to release the charged spring. The motor charges up the spring and is shut off by the "Spring Charged" limit switch. Then the close command actuates the solenoid that releases the spring, closing the breaker quickly.
The molded-case style motors and others without the spring release solenoid can create timing problems when closing. It may take 1-10 seconds for a breaker to close after it receives the close signal. It takes that long for the motor to move the handle or the spring to charge up and release.
For most applications this delay is insignificant, but it is a disaster on a synchronizing circuit. You send the signal when the voltages are in synch, but by the time the breaker closes, the generator has swung out of synch.
Make sure your application is using the correct style of motor operator.