There is an existing AC Condensing unit currently served by #4 copper conductors and a 70A,3p circuit breaker. This unit is being replaced by two smaller units each rated for (208V,3ph, MCA: 33).
I would like to reuse the existing feeder (#4 conductors) to serve both new condensing units by tapping it with two disconnect switches.
From what I understand, this is code compliant and Article 440 has to be followed to make sure the wire size is large enough, the breaker size and to size the disconnect switches.
I was a little confused while reading through article 440. Please verify my calculations below to size the wire, breaker and disconnect switches. Any comments/guidance would be much appreciated.
Since MCA is given I believe I can multiply by 80% to get the full load amps of each unit. 33X0.8=26.4A.
Feeder conductor size: 26.4X1.25 + 26.4 = 59.4. The #4 conductors are rated for 85A so it can be used.
Circuit breaker size: 26.4 x 1.75 = 46.2, round down to 45A OCPD
45A+26.4A=71.4A, round down to a 70A breaker. So the existing breaker can serve both units.
Disconnect for each unit: 26.4X1.15=30.36, next higher size is 40A, so 60A fused disconnect switch with 40A fuses.
MCA is 33A, so #10 conductors would be used to tap the feeder in order to serve each condensing unit.
I would like to reuse the existing feeder (#4 conductors) to serve both new condensing units by tapping it with two disconnect switches.
From what I understand, this is code compliant and Article 440 has to be followed to make sure the wire size is large enough, the breaker size and to size the disconnect switches.
I was a little confused while reading through article 440. Please verify my calculations below to size the wire, breaker and disconnect switches. Any comments/guidance would be much appreciated.
Since MCA is given I believe I can multiply by 80% to get the full load amps of each unit. 33X0.8=26.4A.
Feeder conductor size: 26.4X1.25 + 26.4 = 59.4. The #4 conductors are rated for 85A so it can be used.
Circuit breaker size: 26.4 x 1.75 = 46.2, round down to 45A OCPD
45A+26.4A=71.4A, round down to a 70A breaker. So the existing breaker can serve both units.
Disconnect for each unit: 26.4X1.15=30.36, next higher size is 40A, so 60A fused disconnect switch with 40A fuses.
MCA is 33A, so #10 conductors would be used to tap the feeder in order to serve each condensing unit.