This issue is with a chilled water pump that is controlled by a VFD. The Chilled water pump is 208 3phase 15 hp with a FLA of 37 amps. At 59.5 Hz it is running at 47 amps. I checked the line voltage and it is measuring 205v. The voltage on the load side of the VFD is 199. I would have thought that being that close the the 60 hz that the voltage would be closer to 205. The current reads the same on all legs. The voltage reads the same on all legs. So I don't think we have a phase loss. I would think that there is a problem with the VFD or that there is for some unseen reason too much load on the motor. Does anyone have any Ideas?