And keep in mind, (4) panels fed with 4/0 would not be a true 800 amp service. Rather, a 640.
what size AL conductors XHHW should be used for 4 parallel runs to a CT and on to 4 200 amp disconnects in a residetial service? And since "the lugs are only rated for 75 degree C" can 90 degree C conductors be used to increase the ampacity for a smaller wire size?
I don't think so since they are being feed from a CT cabinet. I have done one home that had a 1200 amp service.is that 800 for a multi dwelling?
I don't think so since they are being feed from a CT cabinet. I have done one home that had a 1200 amp service.Ridiculous but that's what it took.
WOW, it really took a 1200-amp service? That's not a home, it's a hotel, lol.
My old bosses home ............ 26,000 Sq ft. :roll:
Well the entire estate was fed from the 1200 amp service. The house had 600 amps for a 7,000 sq. ft home- probably 400 amps would have worked but originally it was all electric heat. There was a 4,000 sq.ft car museum with a 400 amp feeder. A huge conservatory that was conditioned- 200 amp feeder. A swimming pool with cabana- kitchen and all- 200 amps. Tennis courts and gazeebo-- 200 amps and a utility type garage where the generator and panels hid. In all there were, I believe, 13 heating/cooling systems on the estate- not counting the hydro floor heat in part of the home.WOW, it really took a 1200-amp service? That's not a home, it's a hotel, lol.
How many people lived in it?
2 adults, 2 children.
Did PoCo feed just one service to 1 building?
What voltage/phase?
Must be some large feeders to compensate for voltage drop (if the property has only 1 transformer).
WOW!
[SIZE=""]
Kind of makes me feel poorer than I already am. :roll:[/SIZE]
So does the OP actually have 1 service or 4 ? If only connected at transformer this looks like 4 services