Electron_Sam78
 - Palm Bay, FL
According to 250.56 ground rods need to be resistance tested in reference to earth and not be more than 25 ohms. It says that if this standard is not met another rod should be installed.
Does this mean that if you can't test it you can just install two rods right off the bat and then be in compliance or are you required to test it and install rods until the 25 ohms is achieved? I thought it was the former until I was perusing the article the other day (and I was looking over the book from a grounding course I took a few years back) and saw the language in the section which seems to indicate the latter where it says , "Where multiple...electrodes are installed to meet the requirements of this section..." The grounding class I took taught that multiple electrodes were installed and tested until 25 ohms or less was achieved.
If the intent of the code was only 2 rods wouldn't it say "...two...electrodes..." instead of using the word multiple?