Hello all, and thanks for looking in on this.
I have a 3 phase-4wire multi wire branch circuit that originates in a 120/208V-WYE panelboard. There are several of these and they are all quite long. I have been calculating voltage drop for the conductors and have been doing so based on the circuit being a 3-phase circuit, unbalanced. Is this correct? Or should I be calculating Vd for each individual 120V circuit as though they were all 120V single phase loads. I assume that the formula for 3-phase, 4-wire balanced circuits is out of the question, but my gut is telling me that since all 3 phases are in a single cable assembly with the shared neutral (12/4), I can treat this as a 3-phase circuit and use the 3-phase Vd formula.
My brain stopped working about 10 mins ago so forgive me if the question is a stupid one.
I have a 3 phase-4wire multi wire branch circuit that originates in a 120/208V-WYE panelboard. There are several of these and they are all quite long. I have been calculating voltage drop for the conductors and have been doing so based on the circuit being a 3-phase circuit, unbalanced. Is this correct? Or should I be calculating Vd for each individual 120V circuit as though they were all 120V single phase loads. I assume that the formula for 3-phase, 4-wire balanced circuits is out of the question, but my gut is telling me that since all 3 phases are in a single cable assembly with the shared neutral (12/4), I can treat this as a 3-phase circuit and use the 3-phase Vd formula.
My brain stopped working about 10 mins ago so forgive me if the question is a stupid one.