rochaconstruct
Member
What happened to the requirement for bonding bushings on conduit over 1 1/4" in size
Wasn't that just bushings ?What happened to the requirement for bonding bushings on conduit over 1 1/4" in size
The bushing requirement was for conduit containing wire #4 and larger, rather than by conduit size. Don't have the book handy for reference though.
I think the 1 1/4" rule is from a long time ago, I seem to vaguely remeber it
For years I was told that 1" conduit requied a bushing, but then I realized that was someone had heard wrong and that was probably the size you need to run #4 in.
I was told that also...My old boss said anything over 3/4 required a bushing....He also told me it was ok to tap a branch circuit down one size up to 12''....He called it the 12 '' tap rule....Needless to say neithert of them are in the code book, but I did it like this until I actually read it.