hi all,
i'm a bit confused on NEC chiller cable sizing. my chiller has
RLA = 160A
MCA = 360A
MOP = 500A
my understanding is that the cable is sized per MCA, so a 500 MCM cable would be appropriate here. the OCPD is sized to MOP? or sized to protect the cable within 125%, so somewhere between 360A and 450A (which ever is the standard size).
i always thought that MCA = RLA * 1.25, but the math doesn't work out in this case. is this because RLA is just the motor and not the "system" (the chiller is made up of all sorts of internal components, motors, compressors, etc.)
if i were to run this chiller flat out at max, then put a current meter on it, what would it read, the RLA number? MCA ?
thanks for the clarification!
RLA = 160A
MCA = 360A
MOP = 500A