1971 .
I'll see your 1971 and raise you 1965. 215-7.
This is a specific requirement in the feeder article. The laundry branch-circuit grounding was required in 1947, which might have implied a feeder EGC, but . . . :roll:
But 250-5 is to connect the system to the earth.Doesn't say it's required. Just says to run it if it is required. I'm going by 250-5 of the '71. Prior to that, it was only required to be grounded if it could be done.
That is 215-7, in 1965, as far as I know.hey all-
how long has an egc been required to be installed/run with a feeder?
thanks!
That is 215-7, in 1965, as far as I know.![]()
Where a feeder supplies branch circuits in which grounding conductors are required, the feeder shall include or provide a grounding means.......
And here's what it says:
So it doesn't say you always need a ground. Only if the BCs need grounded.
1892 – NYBFU prohibits the grounding of electrical systems and requires existing systems to be removed from service.
1897 – Mandatory grounding of Lightning Arrestors only.
1899 – Grounding becomes permitted but not required.
1901 – NEC Rule 13A contains provisions for grounding.
1903 – “May be grounded” changed to “should preferably be grounded.
1913 – First code edition to mandate the grounding of one circuit conductor of a service.
1918 – First code edition prohibiting the grounded circuit conductor to be bonded to equipment – Rule 15A.
1962 – First code edition requiring equipment grounding for branch circuits.