I'm not speaking for Bob but all grounding electrodes present must be used therefore if the new addition has the 20' of 1/2" rebar in it, it must be connected to the existing grounding electrode system via #4 copper.
What must be done if you have a metal building that has individual footings for each column (all with re-bar, I think they are 6' square x 6' deep)?
I'm not speaking for Bob but all grounding electrodes present must be used therefore if the new addition has the 20' of 1/2" rebar in it, it must be connected to the existing grounding electrode system via #4 copper.
Is there a minimum foundation size for the requirment of bonding the rebar?
RE: Additions.
Ok , a 1970 new england home (ranch) with an existing service and an existing electrode system. we are contracted to provide wiring for a small addition with 20' of 1/2 '' rebar or more in its foundation, and a 200 amp service up grade. must i ground or bond the rebar of the new foundation ?