I ran a call the other day at a farm. They were on a generator no utility power at all.
They have two generators and a transfer switch so they can shut down one genset to be serviced and still have power.
The problem is that 40 plus old gernerator is rated at 120/240v three phase. 22kv.
The second generator only a couple of years old is a 120/208v. This is the genset that runs most the time. and was running at the time of the visit. The distribution panels are using all three legs at 120v with the exception of a couple of two pole motors and a 3 pole well pump.
my question is how can you use all three legs with the 120/208v genset and then shut down the 120/208v genset for service ( change oil ) and fire up the old genset that is 120/240v without having one "high leg"
Is there some way that 120/240v generator is wired to provide 120v to ground on all three legs? Otherwise every time they would do a oil change they would send 208v on anything that is connected to the stinger!
Could they have re-wired the generator and made it a WYE ? somehow capping off the center tap. and then grounding one end of each of the windings.
Is this possible?
They have two generators and a transfer switch so they can shut down one genset to be serviced and still have power.
The problem is that 40 plus old gernerator is rated at 120/240v three phase. 22kv.
The second generator only a couple of years old is a 120/208v. This is the genset that runs most the time. and was running at the time of the visit. The distribution panels are using all three legs at 120v with the exception of a couple of two pole motors and a 3 pole well pump.
my question is how can you use all three legs with the 120/208v genset and then shut down the 120/208v genset for service ( change oil ) and fire up the old genset that is 120/240v without having one "high leg"
Is there some way that 120/240v generator is wired to provide 120v to ground on all three legs? Otherwise every time they would do a oil change they would send 208v on anything that is connected to the stinger!
Could they have re-wired the generator and made it a WYE ? somehow capping off the center tap. and then grounding one end of each of the windings.
Is this possible?