This same design includes single 350's with 350AT/400AF OCP; I wonder what "AT" and "AF" stand for? Automatic Trip? Either way the 350's seem to barly comply with the AT but not the AF?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Thanks guy's, I wanted something more than a fine print note. I am questioning a design that includes parallel 350's with 600A OCP

I don't see a problem with parallel 350's from a 600A OCP. Parallel 350's is 620 Amps (without derating.) Unless maybe the parallel sets are installed in the same conduit.

This same design includes single 350's with 350AT/400AF OCP; I wonder what "AT" and "AF" stand for? Automatic Trip? Either way the 350's seem to barly comply with the AT but not the AF?

"AT" is Amp Trip and "AF" is Amp Frame. The single set of 350's from the 350A OCP could be a problem, depending on what the load being served is. For instance, it'd be OK on a chiller unit with a MCA of 300 and an MOCP of 350.
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
This same design includes single 350's with 350AT/400AF OCP; I wonder what "AT" and "AF" stand for? Automatic Trip? Either way the 350's seem to barly comply with the AT but not the AF?
350 AmpTrip 400 AmpFrame Breaker
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
310.16 75 degree column for 700kcmil = 460A, 240.4(B) = up to 500A. Am I missing something obvious?

Yes, you are missing something obvious. You said PARALLEL sets of 350's.

From Table 310.16,75 deg column, 350mcm has an allowable ampacity of 310 Amps. Two sets in parallel would have and ampacity of 310x2 or 620 Amps.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Parallel 350 KCM are not equivalent to 700KCM. Very different because their is more surface area on two sets of 350 KCM. As David and others have said-- Look up the amps for 350KCM @ 75 C and double it.
 

tryinghard

Senior Member
Location
California
Parallel 350 KCM are not equivalent to 700KCM. Very different because their is more surface area on two sets of 350 KCM. As David and others have said-- Look up the amps for 350KCM @ 75 C and double it.

Dennis, I was doubling the circular mills. Thanks for catching this and correcting. :grin:
 