Remote 75 kva T/F, not near reliable struct steel, > 5' from water service.
Is it permissible to use the primary feeder's copper equipment grounding conductor inside the primary feeder conduit serving the T/F as (also) the grounding electrode conductor for grounding the T/F if the copper size complies with 250.66? Say a #4 Cu for a 75 KVA 208 delta/wye isolation T/F? Primary
feeder is 3 # 3/0 Cu.,-2" C.
Is it permissible to use the primary feeder's copper equipment grounding conductor inside the primary feeder conduit serving the T/F as (also) the grounding electrode conductor for grounding the T/F if the copper size complies with 250.66? Say a #4 Cu for a 75 KVA 208 delta/wye isolation T/F? Primary