Anothor motor question

Learn the NEC with Mike Holt now!

Anothor motor question

  • Thermal

    Votes: 2 66.7%
  • Solid State

    Votes: 1 33.3%

  • Total voters
    3
Status
Not open for further replies.

Mike01

Senior Member
Location
MidWest
is there typically a distance limitation a combination starter can be remotely located from a motor? I know VFD's have certian distance limitaitons from VFD to motor but what about a standard FVNR combiantion starter? and on a side note what do you prefer thermal overloads or solid state??
 
is there typically a distance limitation a combination starter can be remotely located from a motor? I know VFD's have certian distance limitaitons from VFD to motor but what about a standard FVNR combiantion starter? and on a side note what do you prefer thermal overloads or solid state??

I don't have any documentation, but I've seen hundreds and hundreds of feet without a problem.
 
The longest I ever worked on was about 1700' for a 200 hp well pump on a VFD. There was about 1300' from the VFD to the well and another 400' down the well. I have done a number of motors on starters in the 1000' range.
 
voltage drop

voltage drop

In these instances unless other wise stated by the vfd manufacturer I have calculated voltage drop and sized the motor leg cable accordingly.I have seen thermal bi-metallic overloads last and work accurately ---once periodically surge tested for over 20 years,i have seen electronic overloads fail,act up erratically and randomly in 4-5 years of use,they do offer a wider spectrum of features,this can be good depending on application
 