Hello,
I have a few questions about conducting a Power Quality Analysis.
1) What are the Utility companies really required to provide? I am having trouble getting this information from the utility company. I have copied and pasted what they are telling me. I believe commercial/industrial fall into their +/- 7.5% voltage "rule." These are based on 5 min averages though and don't speak to transients of anything less than the 5 min average. Does this mean they can go 1000% as long it is less than a 5 min average? It seems to me the info they're giving me is not the whole story and that there must me a more detailed specification of what they promise to provide (or are required). I'm aware of IEEE std 519-1992/ANSI C.XX (still trying to get a hold of these) but I don't know where it says that the power company is required to uphold these standards and I'm sure different utilities probably play by different rules, unless there is a federal regulation or mandate that I'm unaware of. Here's what they gave me:
TERMS AND CONDITIONS
___________________
VII. VOLTAGE
A. The following definitions apply to terms used below:
Nominal Voltage
-
the reference level of service voltage.
Maximum Voltage
-
the greatest 5-minute mean or average voltage.
Minimum Voltage
-
the least 5-minute mean or average voltage
Urban Areas
-
areas of concentrated electric loads - generally, cities and towns having population of approximately 2500 or more are considered urban areas.
B. The Company will endeavor to maintain the voltages of Electric Delivery Service within the following limits:
1. For Electric Delivery Service to residential locations in urban areas, the variation from nominal voltage to minimum voltage at the Delivery Point will not be more than 5 percent of the nominal voltage, and the variation from nominal voltage to maximum voltage will not be more than 5 percent of the nominal voltage.
2. For Electric Delivery Service to residential locations in all other areas, the variation from nominal voltage to minimum voltage at the Delivery Point will not be more than 7.5 percent of nominal voltage, and the variation from nominal voltage to maximum voltage will not be more than 7.5 percent of the nominal voltage.
3. For Electric Delivery Service to other locations the variation from nominal voltage to minimum voltage at the Delivery Point will not exceed 7.5 percent of nominal voltage, and the variation from nominal voltage to maximum voltage will not exceed 7.5 percent of the nominal voltage.
C. Variations in voltage in excess of those specified arising from causes beyond the control of the Company shall not be considered a violation of this Section VII.
2) Does anyone have any experience with power quality meters? Any of them have software/hardware that is really top notch? If manufacturers names may not be mentioned this can be sent to me in a private message, if that is allowed.
3) I have some data, and having looked at it the rms voltage stays within the +/- 5% of 480V, however there was a few days time period (of the 30 days that data was taken) where the rms was regularly over 504V, but not by more than 10V, which would fall in the +/- 7.5%. I have also noticed a few dips, one very irregular, on one phase down to 300V rms but it only lasted a few cycles at most. I didn't see any of these transients in a high voltage spike or impulse. Since the rms voltage was only really over the 5% or 504V for a couple days I don't know whether its worth the utility investigating changing taps on the their transformer. Anyone care to chime in?
I have a few questions about conducting a Power Quality Analysis.
1) What are the Utility companies really required to provide? I am having trouble getting this information from the utility company. I have copied and pasted what they are telling me. I believe commercial/industrial fall into their +/- 7.5% voltage "rule." These are based on 5 min averages though and don't speak to transients of anything less than the 5 min average. Does this mean they can go 1000% as long it is less than a 5 min average? It seems to me the info they're giving me is not the whole story and that there must me a more detailed specification of what they promise to provide (or are required). I'm aware of IEEE std 519-1992/ANSI C.XX (still trying to get a hold of these) but I don't know where it says that the power company is required to uphold these standards and I'm sure different utilities probably play by different rules, unless there is a federal regulation or mandate that I'm unaware of. Here's what they gave me:
TERMS AND CONDITIONS
___________________
VII. VOLTAGE
A. The following definitions apply to terms used below:
Nominal Voltage
-
the reference level of service voltage.
Maximum Voltage
-
the greatest 5-minute mean or average voltage.
Minimum Voltage
-
the least 5-minute mean or average voltage
Urban Areas
-
areas of concentrated electric loads - generally, cities and towns having population of approximately 2500 or more are considered urban areas.
B. The Company will endeavor to maintain the voltages of Electric Delivery Service within the following limits:
1. For Electric Delivery Service to residential locations in urban areas, the variation from nominal voltage to minimum voltage at the Delivery Point will not be more than 5 percent of the nominal voltage, and the variation from nominal voltage to maximum voltage will not be more than 5 percent of the nominal voltage.
2. For Electric Delivery Service to residential locations in all other areas, the variation from nominal voltage to minimum voltage at the Delivery Point will not be more than 7.5 percent of nominal voltage, and the variation from nominal voltage to maximum voltage will not be more than 7.5 percent of the nominal voltage.
3. For Electric Delivery Service to other locations the variation from nominal voltage to minimum voltage at the Delivery Point will not exceed 7.5 percent of nominal voltage, and the variation from nominal voltage to maximum voltage will not exceed 7.5 percent of the nominal voltage.
C. Variations in voltage in excess of those specified arising from causes beyond the control of the Company shall not be considered a violation of this Section VII.
2) Does anyone have any experience with power quality meters? Any of them have software/hardware that is really top notch? If manufacturers names may not be mentioned this can be sent to me in a private message, if that is allowed.
3) I have some data, and having looked at it the rms voltage stays within the +/- 5% of 480V, however there was a few days time period (of the 30 days that data was taken) where the rms was regularly over 504V, but not by more than 10V, which would fall in the +/- 7.5%. I have also noticed a few dips, one very irregular, on one phase down to 300V rms but it only lasted a few cycles at most. I didn't see any of these transients in a high voltage spike or impulse. Since the rms voltage was only really over the 5% or 504V for a couple days I don't know whether its worth the utility investigating changing taps on the their transformer. Anyone care to chime in?