40A Circuit Through Attic

Status
Not open for further replies.

PWR73

Member
I ran an 40 A Circuit through an attic and for some reason I installed 60-2 NM cable. I can't remember exactly why but at the time I thought it was a code issue. Anyone remember offhand why I might have had to do this. I have been searching through my code book.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Might not have been necessary. Under the '08 Code #8 NM has an (interior) ampacity of 40 amps. The 90? rating is 55 amps which would derate to 41 amps at 131?F
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I don't think A/C units are typically considered continuous loads by defintion, but the circuit must be sized to the MCA which is not less than 125% of the rated -load current (440.32) so it is the same
The circuit ampacity would normally be determined by the MCA listed on the nameplate.
If a load is 40 amps and is continuous then you would need a conductor rated at 50 amps, or a #6 NM.
There is no problem in your installing a #6, but I think most inspectors would look at the A/C unit MCA and assure the cable installed was adequate for that number.
 
Last edited:

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
60/2 must be one very small cable . :grin:

Perhaps it was the ambient temp or you added 125% to the a/c unit where the mca already has 125% added to it.
 

Volta

Senior Member
Location
Columbus, Ohio
But if he ran 6-2 nm cable, whats the problem?

250.122(B) says that any time you oversize your conductors your EGC has to be increased in size proportionally. 6-2 would only have a #10 EGC.

Exactly. If the circuit could have been installed with #8, then we effectively increased the size, so using circular mils, #6/#8 = 1.59 times bigger than needed. So the EGC would also need to be 1.59 times bigger than the #10 we could have used, so 10380 cmils x 1.59 = 16504, so a #8 Equipment Grounding Conductor would be required.

Or, raise the temperature of the attic until a #8 wouldn't be big enough.

Or, increase the size of the OCPD and/or load until a #8 wouldn't be big enough.
 