Is a hub still required when entering the top of an outdoor panel if a liquid tight connecter is being used?
 
Actually, the one I'm talking about is a 3" Metallic Liquid Tight Male Adapter (with the little rubber washer) entering into the top of an outdoor disconnect.
 
If they are listed for use in wet locations, then it is probably acceptable without a hub- 312.2. I would go to great lengths to avoid it, though.
 