"f " factor in short-circuit cals.
ks1
New member
kentucky
Hey,
Can someone explain to me what the "f " factor represents in short-circuit
calculations? Is it the total "load" (for lack of a better word) that the fault sees?
Thanks
It represents the impedence of the bus or cable between the 2 points the fault current is calulated. It is used to determine your Multiplier ("M")
Do you get that k value from your effective z ?in table 9?
No idea what table 9 is, from where???
3? Faults f = (1.732 x L x I)/(C x EL-L)
1? Line-to-Line f =(2 x L x I)/( C x EL-L)
1? Line-to-Neutral f =(2 x L x I)/( C x EL-N)
Where:
L = Length (feet) of circuit to the fault.
C = Constant from C value tables. For parallel runs, multiply C values by the number of conductors per phase.
I = Available short-circuit current in amperes at beginning of circuit.