Commerical lighting is considered continuous and subject to a 125% multiplier. It's obscure. Some snippet in a section that continous loads are subject to 125%. I think I'll crunch these numbers for fun today and see what I get.
Commerical lighting is considered continuous and subject to a 125% multiplier. It's obscure. Some snippet in a section that continous loads are subject to 125%. I think I'll crunch these numbers for fun today and see what I get.
Did you see, though, that the example would take 125% of the larger of either lighting load? I maintain that it is not Code, but still . . .This is true, but I don't think it plays a direct part in Art 220 when using Table 220.12.
Look at the example mentioned (D-3 pg 765 in '08) and you will see they compared the actual load (8500 watts) to the Table 220.12 calculated load (without the 125%) and selected the largest.
(T 220.12 is a "not less than number which in the OPs situation, is a lot larger than his actual load x 1.25)
... a big refrigerator the holds flowers.
runs all the time to keep flowers fresh...
One 240v 35amp AC omitted rarely used...
I was looking around and ran it to this written by the man himself-)
http://ecmweb.com/mag/electric_commercial_load_calculations/
... Assume the general lighting load for commercial occupancies other than guestrooms of motels, hotels, hospitals, and storage warehouses is continuous. Calculate it at 125% of the general lighting load listed in Table 220.3(A)...
-...
The problem is that the NEC does not tell us in Article 220 to calculate it that way, Art. 220 does not refer to Art. 210, and I know of no rule in Article 240 that would do it either.