"f " factor in short-circuit cals.

Status
Not open for further replies.

ks1

New member
Location
kentucky
Hey,

Can someone explain to me what the "f " factor represents in short-circuit
calculations? Is it the total "load" (for lack of a better word) that the fault sees?

Thanks
 

zog

Senior Member
Location
Charlotte, NC
It represents the impedence of the bus or cable between the 2 points the fault current is calulated. It is used to determine your Multiplier ("M")
 

zog

Senior Member
Location
Charlotte, NC
Do you get that k value from your effective z ?in table 9?

No idea what table 9 is, from where???

3? Faults f = (1.732 x L x I)/(C x EL-L)

1? Line-to-Line f =(2 x L x I)/( C x EL-L)

1? Line-to-Neutral f =(2 x L x I)/( C x EL-N)

Where:
L = Length (feet) of circuit to the fault.
C = Constant from C value tables. For parallel runs, multiply C values by the number of conductors per phase.
I = Available short-circuit current in amperes at beginning of circuit.
 