- Connecticut
- Engineer
You literally cannot terminate directly to "listed" fuses, so we must infer the intent of the code when it tells us to do so. You can only terminate to fuse holders or disconnect switches with integral fuse holders.
Can you terminate on a disconnect first and then route to an adjacent set of fuse (holders)? Would that meet 240.21(C)(4)? I'd say not. But it would be OK to terminate to a set of fuse (holders) first and then to an adjacent disconnect. So why would it be OK to terminate on the switch part of a fused disconnect first. It doesn't comply with the language of the code.
If 240.21(C)(4) is applicable only if you terminate on the fuses, then it can never be applied on circuits greater than 150V to ground.
Nonsense. 240.21(C)(4) can be applied to circuits greater than 150V to ground by simply using a c/b instead of a set of fuses.