Can we splice fire pump wiring? because we want to relocate existing fire pump to a different location and want to re-use existing wiring and extend it to new fire pump location. Thanks!
They are not required to have a fire resistance in the electrical room where they originate or in the fire pump room, unless they are otherwise required by 700.9(D).
But they would be required to have the rating where routed through the building.