yellow1342
New member
- Location
- Fremont Ca
Hi new here, working on my Solar installation at my own house.
it's 40 years old house, underground feed, 100A with breaker/combo meter then connect to sub panel with I think #2 3 w/ground wrapped Aluminum.
If I can upgrade to NM 2-3 copper Romex but include all type THHN, THHW #2copper all has 95 amp rating but according NEC 310.60 feeder type copper #2 has 125 amp.
my question is it correct to use Romex 2-3 to replace my Aluminum 2-3? obviously it's better, but how would I convinence Elec inspector that it's good for 100 amp? because 310.60 does not list NM type wire.
Thanks a lot
Philip
it's 40 years old house, underground feed, 100A with breaker/combo meter then connect to sub panel with I think #2 3 w/ground wrapped Aluminum.
If I can upgrade to NM 2-3 copper Romex but include all type THHN, THHW #2copper all has 95 amp rating but according NEC 310.60 feeder type copper #2 has 125 amp.
my question is it correct to use Romex 2-3 to replace my Aluminum 2-3? obviously it's better, but how would I convinence Elec inspector that it's good for 100 amp? because 310.60 does not list NM type wire.
Thanks a lot
Philip