ground rod

Status
Not open for further replies.

newinspector1

Member
Location
NC
If you have a 200 amp panel that goes to a 30 amp sub-panel for a timer for a lagoon would a ground rod be required at both panels. I thought yes, but the electrician thinks not. Who is right?
 

mcclary's electrical

Senior Member
Location
VA
If you have a 200 amp panel that goes to a 30 amp sub-panel for a timer for a lagoon would a ground rod be required at both panels. I thought yes, but the electrician thinks not. Who is right?

Maybe you, maybe him. We need more info. Is the 30 amp sub panel detached from the original structure? If it's on the opposite side of house, (but still attached) then then answer is no, but if it's a post out in yard with a subpanel, or also detached structure w/ subpanel, both of those would require a GES.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
It depends on whether the panel is just one dp breaker or if the panel had more than 2 circuits. If this is simply a 240v circuit and a disconnect out at the lagoon then I say no based on art. 225.30
 

mcclary's electrical

Senior Member
Location
VA
It depends on whether the panel is just one dp breaker or if the panel had more than 2 circuits. If this is simply a 240v circuit and a disconnect out at the lagoon then I say no based on art. 225.30



Even by that description, it's still a seperate structure. So IMO 250.32 (a) applies
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Even by that description, it's still a seperate structure. So IMO 250.32 (a) applies

Yes, but the exception to 250.32(A) would allow you to omit the grounding electrode at the separate building if the building is supplied by a single branch circuit, which is what Dennis was eluding to.

Chris
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Even by that description, it's still a seperate structure. So IMO 250.32 (a) applies
I agree it is a separate structure but if it is just a MWBC then there is no need to use 250.32. Look at the except. to 250.32(a).

250.32 Buildings or Structures Supplied by a Feeder(s) or Branch Circuit(s).
(A) Grounding Electrode. Building(s) or structure(s) supplied by feeder(s) or branch circuit(s) shall have a grounding electrode or grounding electrode system installed in accordance with Part III of Article 250. The grounding electrode conductor(s) shall be connected in accordance with 250.32(B) or (C). Where there is no existing grounding electrode, the grounding electrode(s) required in 250.50 shall be installed.
Exception: A grounding electrode shall not be required where only a single branch circuit, including a multiwire branch circuit, supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the normally non?current-carrying metal parts of equipment.
 

mcclary's electrical

Senior Member
Location
VA
Yes, but the exception to 250.32(A) would allow you to omit the grounding electrode at the separate building if the building is supplied by a single branch circuit, which is what Dennis was eluding to.

Chris

It would not be a branch circuit if it's feeding a 30 amp panel, it would be a feeder. If you want to say it applies to feeders, then a dweliing doesn't need a ground rod, since it's being fed by one big single MWBC.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If there's (ONE) breaker at the fiinal destination,,,,then this is not a branch circuit.
So if I install a non fused disconnect at the structure then then it is a branch circuit. Add the breaker and I must install a ground rod. Hummmm. I think you are correct with the interpretation of code based on the definition of feeder and branch circuit, but it does not make sense. I also don't believe that is the intent of this section. FWIW-- nothing....
 

Electron_Sam78

Senior Member
Location
Palm Bay, FL
So if I install a non fused disconnect at the structure then then it is a branch circuit. Add the breaker and I must install a ground rod. Hummmm. I think you are correct with the interpretation of code based on the definition of feeder and branch circuit, but it does not make sense. I also don't believe that is the intent of this section. FWIW-- nothing....

I agree with mcclary's. The definition of a feeder and branch circuit require a ground rod if there is a breaker or fuse there. It might not be the intent of the CMP but that's what it says. Maybe a suggestion to reword should be made. Something like, Where a building or structure is supplied by a feeder employing only one branch circuit, including a MWBC, then no GES is required.
 