Charlie, I think zappy wants to know why 250.122(B) is there if the breaker size is the same. You can have a 20 amp breaker with #2 wire for VD and you would need #2 as an EGC. He wants to know why if a #12 works fine under normal conditions for 20 amp cir.
If you increase the size of the ungrounded wire, you increase the available fault current, even if attached to the same breaker
A guess: For some cases, is there an assumption of a longer circuit given that you are using the same breaker size?That just caused the overall circuit impedance, in the event of a fault, to be lower than it was before...
Now, tell me, from a physics point of view, why I need to increase the fault current even more, by using a #10 EGC?
This article never made sense to me, and I think it should be dropped. I don?t believe that the physics of the situation supports the requirement.
Consider the following example (NOTE: This is a discussion of physics, not code, so please don?t cite 250.122 back at me):
? 20 amp breaker, #12 wire, ?fairly long run,? total voltage drop at 3.2%.
? Nothing requires me to upsize the conductors (i.e., VD is not a code requirement).
? I infer that there is a low enough impedance in the #12 conductors, including the #12 EGC, to result in a high enough fault current to trip the breaker, should there be a fault at the end of the run.
? Let me emphasize: This is a safe installation, because I have confidence that the OCPD would trip, on a fault. The fault current is high enough already!
? Now I choose to replace the phase conductors with #10. I have not yet biggie-sized the EGC.
? That just caused the overall circuit impedance, in the event of a fault, to be lower than it was before.
? Therefore, the fault current will be higher than it was before.
? Therefore, the OCPD will trip even faster.
? Now, tell me, from a physics point of view, why I need to increase the fault current even more, by using a #10 EGC?
If you use examples from short runs,,,3.2%vd,,,,,,then you're right, it makes no sense. But stretch your wire out 1000 ft, attach to 15 amp breaker, and leave the original 14 guage EGC in place, you very well could have a fault that is not capable of clearing the OCPD witout an upsized ground.
Yes I will mention 250.122 (B) Your opinion, thoughts and theory are great. But what is written shall be enforced regardless of opinions. Submit a proposal to change that section. The problem is (Charlies Rule) you put out information like this and the electrical world on this forum installs per your post. I simply enforce what is written.
I give the members of this forum credit for more intelligence than that.The problem is (Charlies Rule) you put out information like this and the electrical world on this forum installs per your post.
And I simply design per what is written. I was explaining my reason for disliking this code article, and I was asking for a physics-related response.I simply enforce what is written.
What I described was a hot-to-ground fault. If you have a hot-to-neutral fault, then the EGC is not a part of the fault current path.Charlie, what you're saying is correct only if you consider hot-to-neutral faults. However, hot-to-ground faults are also required to be cleared promptly.
You are welcome to your beliefs. But please allow me to point out that you did not contradict, or otherwise comment upon, my description of the physics of the situation.And I believe that is why the EGC must be at least as big as the hot and neutral conductors.
For now that's all we can do. I agree that this sections needs work because it many instances it makes no sense. Writing a singular code section to cover every scenario is where the problem is.