aftershock
- Memphis, TN
is there a code article that prohibits me from combining grounds from different circuits then landing onto the ground bar with 1 wire when needed because they wont reach the bar?
Why don't you just extend the short ground to the bar?
this is a meter put back that i am going on. it was turned down because of grounds combined apparently after a panel upgrade they did not treach the bar
Turned down based on what code reference?
insp. did not give a ref. nor was he here when i came to correct it. I figured there was nothing to prohibit this but figured i would ask just in case. i went ahead and extended all 5 grounds idividually to the ground bar. i do hope my boss follows up on this to find why it was turned down with no ref. to code
grammer mistakes due to typing from a cell phone
He was absolutely incorrect.it was turned down because of grounds combined apparently after a panel upgrade they did not treach the bar
250.122(C) Multiple Circuits. Where a single equipment grounding conductor is run with multiple circuits in the same raceway, cable, or cable tray, it shall be sized for the largest overcurrent device protecting conductors in the raceway, cable, or cable tray. Equipment grounding conductors installed in cable trays shall meet the minimum requirements of 392.3(B)(1)(c).
"Would" should be "may", as EGC sizing is based on OCPD rating. What if on a motor circuit with a 250% rated OCPD? What if the #6 is upsized for voltage drop, connected to a 30A OCPD? A #6 may be required....
For example, if the largest cable in the old box is a #6cu NM, a single #10 cu conductor would suffice for bonding the enclosure and the entire group of circuits.
Whatever! :roll:"Would" should be "may", as EGC sizing is based on OCPD rating. What if on a motor circuit with a 250% rated OCPD? What if the #6 is upsized for voltage drop, connected to a 30A OCPD? A #6 may be required.
I hate to think otherwise.He very likely believes he was correct.