I was recently called to look at a GFCI in the men's room of one of our buildings. It was apparently the cause of a fire alarm pull when someone observed "flames shooting 4-5 inches out of it..." It's obviously burned but hard to say exactly what it looked like at the time.
It was located in a poor location, directly beneath the sink edge and I believe water and/or soap running down the wall was a significant contributing factor. (Sink edge lines up with the H side of outlet.)
The top lugs of the GFCI were not hooked up, so no other outlets in the area were protected. The in/out wires were hooked together (solid core 12GA) and then stranded wire was jumpered to the H and N (also 12GA). No grounding wire was present, but the outlet was bolted to the box, tied to the conduit.
It was on a 20A circuit breaker that did NOT trip.
Since only the outlet was really 'protected', the GFCI didn't really play any role, other than having more components/material to burn. I'm thinking that water created a short between the H and case. All conductors and insulation beyond the GFCI box (into the conduit) show no signs of damage or heating.
Is it possible to melt through a 20GA stranded wire without tripping a breaker?
And while I don't think it's what happened, does a GFCI care about a H-N short?
It was located in a poor location, directly beneath the sink edge and I believe water and/or soap running down the wall was a significant contributing factor. (Sink edge lines up with the H side of outlet.)
The top lugs of the GFCI were not hooked up, so no other outlets in the area were protected. The in/out wires were hooked together (solid core 12GA) and then stranded wire was jumpered to the H and N (also 12GA). No grounding wire was present, but the outlet was bolted to the box, tied to the conduit.
It was on a 20A circuit breaker that did NOT trip.
Since only the outlet was really 'protected', the GFCI didn't really play any role, other than having more components/material to burn. I'm thinking that water created a short between the H and case. All conductors and insulation beyond the GFCI box (into the conduit) show no signs of damage or heating.
Is it possible to melt through a 20GA stranded wire without tripping a breaker?
And while I don't think it's what happened, does a GFCI care about a H-N short?