Last week I was putting a branch circuit neutral wire on the neutral bar and was getting shocked when I touched the neutral bar. The panel is a 200A three phase supplied through a fused disconnect fed from a 480/240 112.5KVA transformer. I opened up the disconnect and found the neutral and ground separated. I opened up the transformer which is fed from a 480V three phase breaker in the MDP. Three ungrounded conductors and an egc coming into the transformer and leaving the transformer are three ungrounded conductors, the same egc (bonded to the transformer case) and a neutral wire on XO. There is no continuity between the bonded egc and the secondary neutral. Since this is a separately derived system I though the neutral and the egc should be bonded together at the disconnect. Also, there was no gec to the building steel from the transformer. Any input?