self-tapper for bonding in aluminum post
tommyrice
I am considering using TEK-5 8/32 stainless screw to attach a lay in lug to an aluminum upright on an above ground pool which we will consider a permanant pool because it is capable of holding more than 42" of water.I know we need to use lugs suitable for direct burial,but am I violating the code by tapping into the 1/16" aluminum post and covering the bonding lug with dirt enen though the screw threads engage the post where they are not in contact with the soil?
I would use a 10/32 tap and a real ground screw
I love tech 5's, In my opinion this is not a application for that screw. I don't understand why you wouldn't drill a hole and use a SS nut, bolt and washer.
I frankly equate it to a stud screw in a box for the EGC.
250.8 Connection of Grounding and Bonding Equipment.
(A) Permitted Methods. Grounding conductors and bonding jumpers shall be connected by one of the following means:
(1) Listed pressure connectors
(2) Terminal bars
(3) Pressure connectors listed as grounding and bonding equipment
(4) Exothermic welding process
(5) Machine screw-type fasteners that engage not less than two threads or are secured with a nut
(6) Thread-forming machine screws that engage not less than two threads in the enclosure
(7) Connections that are part of a listed assembly
(8) Other listed means
Based on the 2008 NEC I don't know if the use of the TEK-5 with 8-32 thread would be a violation as long as the metal of the pole was at least 1/16 of an inch thick.
Pete
response to using regular 10/32 grnd screw
because reg grnd screw is not stainless steel or other material suited for direct burial,I would be reluctant to use it in this scenario
Since I have gone out on a limb here a lot lately on my opinion(s) here, I really don't understand "(6) Thread-forming machine screws that engage not less than two threads in the enclosure"
I spent the afternoon Saturday, trying to understand exactly what that mean!
I got a great refresher as to various types of screw threads but no answer as to what the exact red phrase meant to anything in respects to screw threads!
Now I have seen both course and fine screw threads described (neither were implied as a Tech-5 screw), in the Machicst handbook, this is not a NFPA point of reference. While course and fine are technically defined in other terms as to a what might describe a tech screw might be, its applicaition, is is not listed (but my book is older).
There is a property listing that states what aluminum can handle as being taped. 10 tapes per inch, but this is not a 10/32 or a 10/16 it's just 10 per inch. So that would be a wide course thread as far as I understand it.
With the 2/3rd, I'm still lost.
Good point. But this is above grade. I think it would be fine. Halex and Leviton's screw are both rated for outdoors
my 2 cents....
a tek screw is not a "thread forming machine screw" like you would find on some makes of panel and meter hubs. a thread forming machine screw for example a 10-32, would have tapered threads with a "notch" on one side of the screw to remove any material as it is being installled.
ok...so my lack of experience with tek 5 shows:roll:....that would be a thread forming machine screw from the looks of it. the screws i mentioned in previous post are usually found in flourescent strips and lay in types as the provided ground screw.
I question if it is a good idea on 1/16 inch aluminum to have it tapped, I can see that connection failing in a short time.