200a service upgrade
tommyt
I am going to be installing a 200a service using 2 1/2 gal as the mast. Although I have done several service upgrades this will be the first using galvanized conduit. I was wondering if any additional bonding will be necessary from the weather head on down into the meter pan?
hurk27
Why the 2 1/2"? seems kind of big for a 200 amp? around here we use just 2" our meters won't take a 2 1/2" unless we go to a 320 base.
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
That was what I had on my post but then I thought if it were a 3 phase with 250kcm alum and a neutral he may need 2 1/2"
augie47
Tennessee
A lot of the POCOs here require a 2-1/2" minimum for strength.
The 2" mast stopped after a ice storm about 20 years ago when hundreds of masts buckled.
KWH
Mast Pipe Bond
Mast Pipe Bond
Does your Poco require seperation between mast and meter
tommyt
200a service
200a service
Thanks for all the info. I contacted the inspection outfit I use and they told me to use 2 1/2, I assumed that it was because it is also the point of attachment. I did not think to ask him about any additional bonding at the time so I just thought I would throw it out here and see what was said.
tommyt
200a service
200a service
Just thought I would update you guys. Finished the service today. The 2 1/2 went right into a 2 1/2 hub for the top of the meter and everything else went as usual. It ended up as quite a nice installation. I almost prefer it to pvc.