detached garage sub, with ground rod i think(as opposed to attached garage sub w/o a ground rod). anyway the egc goes down into the rocks, i assume there is a g rod. i will have to dig it up but the subpanel also has a neutral to the home underground. there is no ground wire run to the home (service panel)
the grounds are run with the neutrals and the egc is connected to the no longer floating neutral/ground bar. yea, home owner!
the conduit? into the bottom of the sub is done with plumbing pipe.
i get perfect readings when nothing is on, but as soon as you turn on anything in the garage, you get a phase with about 90V and one at 150V, 240 ptp. when he turned on a 120V compressor across the garage, i was reading a jump from 120 to 240 from hot to N on my light circuit, (not connected to other).
another weird thing. measuring Hot to N in a light fixture with 120V in, i put one meter lead on a hot and the other on the line in N and get 120V. then i put one lead on the hot and the other on the feed out N, WHICH IS KNOWN TO BE 10 FEET LONG AND NOT CONNECTED TO ANYTHING IN THE NEXT LIGHT FIXTURE IN THE ROW, ALL wires in that one disconnected; now my meter lead is basically going nowhere: I READ 120v. why is that?
i plugged in a work light into the garage recept ckt gfi and it was like a 30 watt light bulb. i measured 5 amps coming into the garage on one phase, but NO CURRENT LEAVING ON EITHER THE 'EGC' OF THE GARAGE OR THE NEUT GOING BACK TO THE HOUSE, NOR THE OTHER HOT. shit!
is it possible my neut wire going underground is connected by like one strand or something? how can a wire going into outer space give my fluke meter a voltage reference????? aaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaahhhhh!
i screwed around with this for i'm ashamed to say how long.
tomorrow i am going to run a N wire from the sub to the home panel and see what happened then.
the grounds are run with the neutrals and the egc is connected to the no longer floating neutral/ground bar. yea, home owner!
the conduit? into the bottom of the sub is done with plumbing pipe.
i get perfect readings when nothing is on, but as soon as you turn on anything in the garage, you get a phase with about 90V and one at 150V, 240 ptp. when he turned on a 120V compressor across the garage, i was reading a jump from 120 to 240 from hot to N on my light circuit, (not connected to other).
another weird thing. measuring Hot to N in a light fixture with 120V in, i put one meter lead on a hot and the other on the line in N and get 120V. then i put one lead on the hot and the other on the feed out N, WHICH IS KNOWN TO BE 10 FEET LONG AND NOT CONNECTED TO ANYTHING IN THE NEXT LIGHT FIXTURE IN THE ROW, ALL wires in that one disconnected; now my meter lead is basically going nowhere: I READ 120v. why is that?
i plugged in a work light into the garage recept ckt gfi and it was like a 30 watt light bulb. i measured 5 amps coming into the garage on one phase, but NO CURRENT LEAVING ON EITHER THE 'EGC' OF THE GARAGE OR THE NEUT GOING BACK TO THE HOUSE, NOR THE OTHER HOT. shit!
is it possible my neut wire going underground is connected by like one strand or something? how can a wire going into outer space give my fluke meter a voltage reference????? aaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaahhhhh!
i screwed around with this for i'm ashamed to say how long.
tomorrow i am going to run a N wire from the sub to the home panel and see what happened then.