TOOL_5150
Senior Member
- Location
- bay area, ca
I ran into something I havent seen before, A MWBC with a #12 noodle and a #12 hot and a #14 hot. The house is K&T so it was 3 loom covered wires I was dealing with, the #14 being for the lights.
I was doing a service upgrade [whopping 4 circuits in this house!] I am still on the 2005 NEC, so I used SP breakers. The #14 was protected by a 20A FPE breaker.
When I hooked up my 4 circuits [2 MWBC's] I put both legs of that particular MWBC on 15A breakers. Could I use a 20A on the #12 hot, since the noodle is #12 also, while leaving the #14 leg on a 15A breaker? I am going back tuesday to finish up a few other things, so I could change it then. I just wanted to error on the safe side and used 15A breakers.
~Matt
I was doing a service upgrade [whopping 4 circuits in this house!] I am still on the 2005 NEC, so I used SP breakers. The #14 was protected by a 20A FPE breaker.
When I hooked up my 4 circuits [2 MWBC's] I put both legs of that particular MWBC on 15A breakers. Could I use a 20A on the #12 hot, since the noodle is #12 also, while leaving the #14 leg on a 15A breaker? I am going back tuesday to finish up a few other things, so I could change it then. I just wanted to error on the safe side and used 15A breakers.