Proper name for fuse bucket.
chris kennedy
Miami Fla.
Retired electrician
I have a large MDP with fuse buckets ranging from 400A to 30A. Again preparing a report and need to know the proper name for these sections.
Thanks.
Always called a section the vertical area holding the buckets; the buckets are the buckets far as I know.
if its an indoor switchboard, its probably a Type 1 Enclosure. When we get submittals for switchgear they usually give each enclosure a code, but they are just letters that tell the manufacturer what parts to install I believe, and then of course the fuse or breaker size with Frames size and trip settings.
I usually just call em buckets tho.
'Buckets' for me. Beyond that it's a P/N (manufacturer part number).
For a report it may be ok to refer to section #, and bucket/space#.
How does this look?
Feeder conductors for the VFD controlling AHU1 originate at a 60A fusible section in MDP and consist of three #4 Thhn ungrounded conductors and one #10 cu EGC in 1" EMT fused at 60A. Length of feeder conductors is approximately 40'.
I think I can live with this. Bear in mind this report will go on state records and English is not really my forte.
Thanks all for looking at this.
Trivial, but it is THHN I believe.
Add: Ran it by wife and she understood your paragraph, except "section", Go with what Jim said.
"is" should be "are".
I agree with Jim. When I hear section, I think one vertical column of the MCC that you bolt onto the other sections. I'd probably call it a 60 amp fused bucket as well.
U need to get hold of a Sq D Catolog or the like and where the switch can carry some high rating! Or as they said...
"IS" is the correct word! You are describing the "LENGTH," of which there is only one. "The length are?":confused:
Good Luck!
I've only ever heard it as a Fused Disconnect...
Sorry to the Dots... on the other response.
Square D catalog seems to refer to each vertical column as sections and refers to components installed in them as devices.
In the panelboard section of the catalog they refer to the units of the fused devices panelboards as Branch Switches.
Although 'bucket' is a popular term I am guessing it originated in the field by installers and service people.
Buckets are a common term used with motor control centers. Some people also use it for fusible switches when they are in 'panels' to differentiate them from the 'hang on the wall' ones.