GG
- Ft.Worth, T.X.
422.16(A)and the appliance is intended or identified for flexible cord connection.
If it were allowed that particular cord and receptacle would likely not be the right one to use either. (probably a 10-30 non grounding type instead of a 6-30 grounding type)
That was done around here for awhile. Seems they were wanting to use a 3-wire dryer cord for a disconnecting means. Haven't seen it in years.
Also check out 400.7(A) uses permitted for flexible cords.
I do not see anything in the uses permitted that will apply to a water heater with the possible exception of (8). Most water heaters that will be allowed to be cord connected by (8) will likely have the cord installed on them at the factory.
Does an electric W/H need a disconnect if it, and the panel serving it are both in the garage?
~Matt
I could understand why they were doing it that way if it cost less, but I don't see that costing much difference than installing with a pullout disconnect and up to 3 feet of flex, may even cost more.
If you are within sight of branch circuit overcurrent device you don't even need the disconnect.