Are there any changes to the current NEC as opposed to the 2005 NEC with regards to Residential Load Calculations?
 

480sparky

Senior Member
Location
Iowegia
Look for text highlighted in gray.
sw017.gif
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
From the NECH

Summary of Changes
? 220.52(A): Clarified that the requirement applies to all installed circuits covered by 210.11(C)(1).

? 220.82(B)(2): Clarified that the requirement applies to all installed circuits covered by 210.11(C)(1).

? 220.82(B)(3): Revised to exclude clothes dryers connected to the laundry branch circuit.

? 220.82(B)(4): Clarified that the provision applies only to permanently connected motors not covered in 220.82(B)(3).

? 220.82(C): Clarified that the provision applies to heat pumps.

? 220.83(A)(2) & (B)(2): Clarified that the requirement applies to all installed circuits covered by 210.11(C)(1).

? 220.83(A)(3) & (B)(3): Revised to exclude clothes dryers connected to the laundry branch circuit.

? 220.84(C)(2): Clarified that the requirement applies to all installed circuits covered by 210.11(C)(1).

? 220.84(C)(3): Revised to exclude clothes dryers connected to the laundry branch circuit.