We recently were called in to replace a 45 KVA transformer that is used strictly for an elevator. The elevator is a 460 volt 3 phase unit. The supply to the building is a 120/208 wye system. We replaced the xfmr with the same type that had been working there since 1995, it was a 480 volt Delta primary and 208y/120 secondary. I do get 486 volts across phases for an output but the individual phases to ground are 235v, 259v and 305v. When I put an ammeter on the ground it reads a steady 9 amps. We went through all grounding connections and tightened or repaired them. Input on each leg to ground is 121v per leg and 210 v across phases. There are (3) 3/0 copper conductors and (1) #4 copper grounding conductorfeeding this xfmr. The different output voltages and the 9 amps to ground concern me. Any input?