Commercial 3 phase a/c condenser wiring comes directly off main 3 phase panel without any breaker. This is an old panel that does not have breakers. It only has 1 set of large fuses. This a/c wiring is connected in the main panel after it is fused. It then goes directly from the main panel to a disconnect box on #6. The main and this disconnect are only about 1 foot apart. This disconnect is fused with time delay 60 amp. The load comes off the disconnect on THHN or THWN AWG #8. It runs in conduit about 100 ft to the outside to a non-fused disconnect at the unit.
The condensor has a minimum circuit amp rating of 38.9
What do you think about all of this, especially the #8 carrying the load?
The condensor has a minimum circuit amp rating of 38.9
What do you think about all of this, especially the #8 carrying the load?