3-phase disconnect - 2 fuses
It is a 3-phase system that is from the early 1900's used for an elevator. It comes in from the street to a meter and then to the main disconnect. The disconnect with the two fuses is tapped from the main. The 3rd leg line conductor is attached to a isolated bar. The load for this 3rd leg is also attached to this bar. I heard one "ole-timer" refer to this system as "Chicago 3 leg" or "Delta 3 leg". I am not sure about the accuracy of these names.
It is a corner grounded delta and the grounded phase can not be fused.
Roger
So, if I pull the 2 fuses, the 3rd legg is also dead?
I do a little voltmeter testing first :)
From either fuse to ground you should get a reading (hopefully 240v or 480v), from the 3rd leg to ground you should read "0", thus the name "corner (one phase) grounded"