Hi, I am trying to do a basic fault calculation of a 69KV to 120V transformer and am finding GE specs on the unit confusing. This is not something I have a great deal of experience with so some advice would be great.
The unit is the JVT350. If you are interested a spec sheet is easily located by searching on that model.
Specs:
Primary: 69KV
Secondary 120V
Ratio: 600:1
Thermal rating: 4.5KV
BIL: 350KV
And something I do not understand:
"ANSI Accuracy, Burden Per ANSI, W,X,M,Y = 0.3"
What do I use as the impedance for the fault calculation?
Also, just to confirm, thermal VA is the rated secondary output maximum while maintaining accuracy?
thanks!
Specs:
Primary: 69KV
Secondary 120V
Ratio: 600:1
BIL: 350KV
thanks!