CWillcox
- New Paris, OH
I have been asked to consider changing our site from using divisions to zones.  Has anybody done this before?  If so, what pitfalls did you find along the way?  Lessons learned? Advice?
			What little disagreement I have with squnsel on this is more semantic than substantive. It?s my opinion that the definitions of NEC Zones were ?force fit? into Division definitions and the only significant difference is Zone ?x0? (where ?x? is blank or ?2?) is definitely hazardous under any reasonable active process operating or maintenance condition. (Zone n1 ?may? be hazardous under ?normal? conditions ? but isn?t necessarily)I have been asked to consider changing our site from using divisions to zones. Has anybody done this before? If so, what pitfalls did you find along the way? Lessons learned? Advice?
So Bob, wht's going to happen with the Class/Div. listing of all the equipment in the area?What little disagreement I have with squnsel on this is more semantic than substantive. It?s my opinion that the definitions of NEC Zones were ?force fit? into Division definitions and the only significant difference is Zone ?x0? (where ?x? is blank or ?2?) is definitely hazardous under any reasonable active process operating or maintenance condition. (Zone n1 ?may? be hazardous under ?normal? conditions ? but isn?t necessarily)
That being said, in NEC jurisdictions you only need to change the current area classification document?s legend from Division 2 to Zone x2 and Division 1 to Zone x1 then identify the interior of tanks and such as Zone x0 (where there probably isn?t any wiring anyway) and you?re done.
Well, not quite. Here is where the real problems start. The Groups and ?T-Classes? don?t match up nearly so well. See Section 500.8 (B) (1) for the significance. Note the requirement is for ??specific gas, vapor, dust, or fibers/flyings that will be present.? Then compare the ?Group? definitions in 500.6 to those in 505.6. For a complete education compare the ?T-Classes? of various materials per Divisions and Zones in NFPA 497 or 499.
The only significant benefit to NEC Zones is the ability to use the ?Increased Safety? (AEx e) protection technique in Zone 1. The other protection techniques permitted in Zone 1 are already effectively permitted in Division 1 or are generally unavailable commercially; e.g. AEx q.
Excellent question. A lot of equipment originally designed for US domestic Division applications are now marked with both schemes.So Bob, wht's going to happen with the Class/Div. listing of all the equipment in the area?
Section 505.9 (C)(1), permits Division listed equipment to be Zone marked automatically with a few restrictions. Note though, the "few restrictions" are very specific requirements in 505.9 (C)(1)(2)&(3) to match Zone Groups and Temperature Classes. As I said in my original response, they don't line up nearly as well. While dropping the alpha part of the T-code usually works, it isn't necessarily absolute for the ?? specific gas...that will be present? - and matching Groups can still be a real bear altogether.
CMP14 was able to force-fit Zones into Divisions only because most Panel members were ignorant of (and the ones that weren't ignorant deliberately ignored) the fundamentals of classic IEC Zone based electrical area classification. That's why they originally required a PE to do the area classification; but that offended the "User" Panel members that weren't PEs and has since been dropped.
In my opinion, reclassifiying Divisions to Zones is a very dangerous proposition; nevertheless, it can be done if one knows what they are doing. Trying to determine if existing equipment only marked for Division is suitable for a location reclassified to Zones is not a trivial exercise - no matter what the manufacturers' try to tell you.
I feel that the introduction of the Zone'd installation was unnecessary and that it weakens the overall safety of the Chemical industry.