In an HVAC unit with multiple compressors, fans, etc, are the fla, lra, and rla amperage ratings on the data plate cumulative or per?

Thank you.
 
In an HVAC unit with multiple compressors, fans, etc, are the fla, lra, and rla amperage ratings on the data plate cumulative or per?

Thank you.

Do you need to know more than the MCA and the Maximum Overcurrent Protection Device size?

Welcome to the forum. :)
 
You should find the MCA and the Maximum Overcurrent Protection Device size
on the name plate for the unit.
 
I would think that a single nameplate on the unit refers to the unit as a whole.

(I'd be very grateful to the manufacturer for sticking one on. ;))

And, ditto on the welcome! :)
 