gumbey1@yahoo.com
Does the nec allows the neutral conductor(grounded conductor) to pass through the switch box?
May be i did not explain enough about my question in the first instant,let me try again.When doing the conduit work for lighting you should leave the panel and enter the receptacle then to the switch ,in this instant you avoid the nuetral passing through the switch box.But if you conduit from the panel to the switch then to the receptacle you cannot avoid the the nuetral passing through the switch box.This is why ask the question.
The 2011 will only require a grounded neutral conductor in a switch box where the wiring method is a cable. If the wiring method employed is a raceway or conduit then a grounded neutral conductor will not be needed in the switch box.
This is because it would be fairly easy to pull a neutral to the switch box if down the road it was need for a dimmer or occupancy sensor.
Chris
Will they require room in the raceway for the neutral if it is someday needed? Raceway with max fill otherwise would not allow for adding it.
Not that I have a habit of pulling max fill capacity to switch drops but it could happen.
Switch boxes with multiple circuits require multiple neutrals I would assume.
(C) Switches Controlling Lighting Loads. Where switches control lighting loads supplied by a grounded general purpose branch circuit, a grounded circuit conductor shall be provided at the switch location. [ROP 9-95]
Exception: The grounded circuit conductor shall be permitted to be omitted from the switch enclosure where either of the conditions in (1) or (2) apply: [ROP 9-95]
(1) Conductors for switches controlling lighting loads enter the device box through a raceway. [ROP 9-95]
(2) Cable assemblies for switches controlling lighting enter the box through a framing cavity that is open at the top or bottom on the same floor level, or through a wall, floor, or ceiling that is unfinished on one side.[ROP 9-95]
Why should you enter the receptacle first and then go to the switch?