Andy Sherrill
I am working on adding an 8750 sq ft office area to an existing strip mall type building.  The existing service is 240 V, 3 phase, closed delta (high leg).  I plan to feed all of my three phase loads from one panel.  All of the office lighting and receptacles will be fed from single phase panels.  I am trying to decide if I need to size the neutral for 200% of the phase conductors?
Even though these are single phase panels, this is a three phase service, so I assume the harmonic currents will still add? Also, with this type of service, there will be significant "normal" current on the neutral due to the inherent imbalance. The load for the single phase panels will be almost all non-linear. All lighting is fluorescent. The receptacle load will be PCs, copiers, printers, etc. There is also a server that will be fed from one of these panels. I am sure the owner has a UPS for the server. These panels will probably not be heavily loaded. They will be 200 A panels. My calculated load is around 135 A. The load will probably be musch less under normal circumstances due to the large number of receptacles.
Another question I have is if the neutral conductor needs to be sized for 200%, doesn't the panel neutral also need to be sized for 200%?
Thanks for your help!