16' of baseboard heat @ 250watts/ft = 4000w
4000w @ 240v = 16.6amp
NEC 424-3(b) 125% = 25amp Breaker
NEC 240.3(b) = 12/2nmb wire
Look Correct?
16' of baseboard heat @ 250watts/ft = 4000w
4000w @ 240v = 16.6amp
NEC 424-3(b) 125% = 25amp Breaker
NEC 240.3(b) = 12/2nmb wire
Look Correct?
Yes, 240.4(D) tells you you can't use the ampacity in the table for #12. It must be for a 20 amp load in the case of a baseboard heater.240.4 (D)![]()