Baseboard Heat Load
DJMJ
16' of baseboard heat @ 250watts/ft = 4000w
4000w @ 240v = 16.6amp
NEC 424-3(b) 125% = 25amp Breaker
NEC 240.3(b) = 12/2nmb wire
Look Correct?
Look Correct?
DJMJ, welcome to the forum!
Your numbers are good, but it is 240.4(D)(5) that will stop you from using #12.